EUC storage & charging cabinet with fire suppression system


Recommended Posts

As beautiful as to be expected from the same mind that created/maintains EUC World. Well done.

Link to post
Share on other sites
  • 2 weeks later...

Very slick. I like the automatic garage door opener option. I was reading a pdf the other day about the gases from these events and was shocked at just how toxic they are. Everyone knows they are to be avoided but the lethality within a confined space was extraordinary.

Link to post
Share on other sites
16 minutes ago, DavidB said:

I was reading a pdf the other day about the gases from these events and was shocked at just how toxic they are. Everyone knows they are to be avoided but the lethality within a confined space was extraordinary.

Number one lethality of beeing with something burning/(heavily) smoking should be the lack of oxygen. Maybe supported by carbonmonoxide.

And some passing out from catbondioxide before dying...d

Additiinally i'd consider fumes from about almost eberything in a household like electronics, plastics, ... as extremely toxic.

Or is there something even worse within the li ion batteries?

Link to post
Share on other sites

Yes HF.

1.7 mg/m3 Allowed exposure level at work in Sweden

25mg/m3 IDHL

139mg/m3 The lethal 10 minute value ((AEGL-3)

A fire that consumes a 2kw li-ion battery emits b/w 40 and 400gm of HF according to this pdf. That would be 40000mg/90m3 for a 6mx6mx2.5m garage. That is 444mg/m3 or 3 times the lethal 10min level at the lower emission and 10x that (ie 30x lethal dose) at the higher level.

Like I said in my previous post I was shocked by the data.

 The pdf is "Thermal propagation in lithium ion batteries" at ec.europa.eu page 16 on..

The same pdf stated that if the gases released from pre-ignition venting are confined an explosion can occur on ignition. I have no idea how probable this would be. But LTO batteries are looking like the weight may be a acceptable trade-off when considering there high discharge rate and fast charging.

Link to post
Share on other sites

A short video from a test run of fire suppression system:

This was initiated manually from control panel. This test proved design assumptions - water spray discharge at ~20 liters per minute under water supply of about 2.2 bar (1.5 bar at sprinkler line) :thumbup:

Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...